N series Recloser Problem Solving Advise
2
3
Problem Description/
Possible Reason/
Test to be done/Solution/
4
Uraian MasalahKemungkinanTest harus dikerjakanPenyelesaian
5
Microprocessor lightFaulty OCPMUsing lap top PC and WSOS Software,Replace OCPM
6
on operator panel is try to go on-line. If WSOS goes on-line
7
not flashingsuccessfully - it indicates that CAPM
8
is functional.
9
Lampu microprocessor
10
di Operator panel me-Kerusakan pada Gunakan lap top PC dan SoftwareGanti OCPM.
11
nyala, tapi tidak "ke-OCPM (OperatorWSOS, coba on-line ke OCPM. Jika
12
dap kedip".Control Panel Mo-berhasil, hal ini mengindikasikan bah-
13
nitor)wa CAPM berfungsi.
14
15
No Power SupplyCheck that battery and auxiliary supplyIf power supply
16
to CAPMMCBs are turned ON, check the batteryvoltage low - replace
17
and auxiliary supply voltage.the batteries and re-
18
store aux. Supply.
19
20
Tidak ada suplaiPeriksa MCB untuk batere dan auxiliaryJika tegangan power
21
power ke CAPMapakah ON, kemudian ukur tegangan-suplai rendah - ganti
22
nya.batere dan nyalakan
23
auxiliary 110 atau 220VAC kembali aux. Suplai.
24
Batere normal 24 ~ 27 VDC.
25
26
Faulty CAPMCheck power supply voltage and attemptIf voltage is normal
27
to go with WSOS on-lineCAPM doesn't
28
respond to WSOS -
29
replace CAPM
30
31
Kerusakan CAPMPeriksa tegangan catu daya dan cobaJika tegangan normal
32
aktifkan WSOS.CAPM tidak meres-
33
pon WSOS - ganti
34
CAPM.
35
36
Unable to close theLow power supplyCheck that panel can be turned ON. Turn MCBs ON, con-
37
RecloservoltageCheck that battery and auxiliary powerfirm that the voltage
38
supply MCBs are turned ON and poweris within the specifi-
39
supply voltage is normal.ed range. Replace
40
the betteries if
41
necessary.
42
43
Recloser tidak mau diTegangan catuPeriksa bahwa panel dapat di ON.ON-kan MCB, pasti-
44
masukan (ON-kan).daya rendah.Periksa MCB untuk batere dan catu kan tegangan sesuai
45
daya tambahan dalam keadaan ON, danrange dari spek.
46
tagangan catu daya normal.Ganti batere jika di
47
perlukan.
48
49
50
51
52
53
Problem Description/
Possible Reason/
Test to be done/Solution/
54
Uraian MasalahKemungkinanTest harus dikerjakanPenyelesaian
55
Recloser is notCheck that system status (page 2) If system status
56
connected to shows "ACR Connected"displays "ACR
57
control cubicleunplugged" - check
58
(PTCC)that control cable is
59
plugged in correctly.
60
61
Recloser tidak terPeriksa sistem status (page 2) menun- Jika sitem status
62
hubung ke controljukkan "ACR Connected"menunjukkan
63
cubicle (PTCC)."ACR Unplugged"-
64
periksa plug kabel
65
kontrok P1 tersam-
66
bung dengan benar.
67
68
Open circuit forCheck the resistance between pins 21 -Check control cable
69
auxiliary travel11 (aux switch, indicates ACR tripped)(continuity test) if
70
switch in controland pins 22-11(aux switch, indicatesboth microswitches
71
cable.ACR closed). One of this switches show open circuit.
72
should be closed (depends on the status
73
of recloser).
74
75
Rangkaian terbu-Periksa tahanan antara pins 21 - 11(sak-Periksa kabel kontrol
76
ka untuk auxiliarylar bantu mengindikasikan ACR trip) dan(tes kontinyu) untuk
77
travel switch padapins 22-11(saklar bantu mengindikasi-memastikan kedua
78
kabel control.kan ACR tutup/close). Satu dari saklar"microswitch" ini ter-
79
bantu ini harus tutup (tergantung statusbuka.
80
dari recloser).
81
82
Open circuit forMeasure the resistance on the relevantContact Customer
83
aux travel switchpins (same numbers) of the SCEM cardService Schneider
84
in internal loom.with control cable disconnected.Indonesia.
85
86
Rangkaian terbu-Mengukur tahanan pins pada SCEMHubungi CST PT.
87
ka untuk saklarcard dengan kabel kontrol di lepas dariSchneider Indonesia
88
bantu pada inter-plug-nya.021-7504406 atau
89
nal loom.021-7504598
90
031-8288333
91
Recloser is in "DoCheck the configuration for recloserSet recloser to Local
92
not operate"modemode and/or status of Work Tag./remote control as
93
or "Work tag" isre quired and/or re-
94
applied.move Work Tag. Or
95
change Work Tag
96
Applied to Off.
97
98
99