FINAL PROTOCOL WORKSHEET for Ventilation Systems: DESIGNCopyright
PHPP 1998-2022
Passivve House Institute
2
Supply- / Extract-Air Ventilation System with Heat RecoveryVersion 10.4
3
4
Project
Ventilation Planning
5
Object:Company:
6
Location Street, No.:
Person in Charge:
7
Location Postcode, TownStreet, No.:
8
Building Owner Name:
Postcode, City:
9
Building Owner Phone No.:Phone No.:
10
Year of ConstructionDate:
11
Signature:
12
Standard use or special requirements:
13
Dimensioning of the ventilation system according to standard use conditions
14
15
2. Criteria for dimensioning the airflow volumes
16
reference values
number
resulting starting values
17
fresh air demand:
18
per person:30m³/h x =m³/h m³/h
19
20
extract air demand:
21
kitchens:60m³/h x =m³/h
22
bathrooms, utility rooms etc.:
40m³/h x =m³/h
23
WC, storage, etc.:20m³/h x =m³/h
24
sum:m³/h m³/h
25
26
starting value nominal airflow (standard operation):
m³/h
27
28
3. Distribution of the airflow volume flow rate
29
Nr.RoomAreaClear HeightRoom VolumeAir Volume Flow RateAir Change RateType of Flow-Off Vent
30
(each valve individually)AhA x hVSUVEXVTHROUGHn(door gap, grid in door leaf
31
mm³/hm³/hm³/h1/hdoor frame, valve …)
32
1
33
2
34
3
35
4
36
5
37
6
38
7
39
8
40
9
41
10
42
11
43
12
44
13
45
14
46
15
47
16
48
17
49
18
50
19
51
20
52
sum:------
53
54
4. Adjusted airflow volumes, control range
55
base ventilation:
m³/h
at least 30% below nominal airflow volume
56
nominal airflow volume:
m³/h
fresh air demand, at least 0.3-fold air change rate
57
peak ventilation:
m³/h
at least 30% above nominal airflow volume
58
ventilated area:
59
ventilated volume:
60
nominal airflow volume, sum:
1/h
61
62
5. Efficiency requirements
63
ventilation unit (manufacturer, product):
64
efficiency of heat recovery:
75%
(according to PHI testing method for the PHPP)
65
max. power consumption in nominal operating mode:
0.45W
(for fans and control)
66
67
6. Requirements for noise protection
68
A-weighted noise pressure level of the unit in the living space:
25dB(A)
69
A-weighted noise pressure level of the unit in the installation room:
35dB(A)
70
71
7. Hygienic requirements
72
fresh air filter:F7
first link in the chain, if applicable before subsoil heat exchanger
73
extract air filter:G3
at least bathroom and laundry rooms; recommendation: all extract air rooms
74